Question 12085 of 871 · Maryland Journeyperson Electrician Exam
A 28-unit building has one 12 kW range per unit. What is the range demand load under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12085
- A: 43 kW
Explanation
For 26 to 30 ranges, Column C equals 15 kW plus 1 kW per range: 15 + 28 = 43 kW (Table 220.55).