Under the NEC 2020 or 2023, an 8 kW cooktop and a 4 kW wall oven in the same kitchen are on one branch circuit. What is the branch circuit load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12087
- C: 8 kW
Explanation
Table 220.55 Note 4 lets the nameplates of a counter-mounted cooktop and up to two wall ovens in the same room be added and treated as one range: 8 + 4 = 12 kW, which takes 8 kW from Column C.