Question 12094 of 749 · Maryland Journeyperson Electrician Exam
NEC 2020/2023 220.83(B): an existing 2,000 ft2 dwelling (two small-appliance and one laundry circuit, 11 kW range, 5.5 kW dryer) adds a 6,000 VA central AC. What is the calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12094
- B: 21,600 VA
Explanation
Where heating or AC is added, that load counts at 100 % (6,000 VA). The other loads, 27,000 VA, take the first 8 kVA at 100 % and the remainder at 40 % = 15,600 VA. Total 21,600 VA.
More questions: Load Calculations