What is the ampacity of 4 AWG THWN copper (75 °C insulation) with three current-carrying conductors at an ambient of 45 °C?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13050
- B: 69.7 A
Explanation
THWN is a 75 °C insulation, so the base ampacity is 85 A and the 75 °C correction factor for 41 to 45 °C is 0.82: 85 x 0.82 = 69.7 A. Using the 90 °C factor 0.87 gives 74.0 A, which does not apply to THWN.
More questions: Electrical Calculations
- 13051Four current-carrying 3/0 AWG THWN-2 copper conductors are installed in a raceway where the ambient is 50 °C. What is the derated ampacity from the 90 °C column?
- 13052Six current-carrying 8 AWG THHN copper conductors are in one raceway at 30 °C ambient, and all terminations are rated 75 °C. What is the maximum ampacity that may be used for each conductor?
- 13053Three current-carrying 2 AWG THHN copper conductors are installed at 35 °C ambient and terminate on 75 °C rated lugs. What is the maximum load current the conductors may be used for?
- 13054A raceway contains two 3-phase, 4-wire wye circuits, and the loads are mainly electronic (nonlinear), so the neutrals count as current-carrying. Equipment grounding conductors are also present. What adjustment factor applies?
- 13055A raceway holds three 120 volt, 2-wire branch circuits, each with its own neutral, plus one equipment grounding conductor per circuit. How many current-carrying conductors are counted for adjustment?
- 13056A raceway contains three 120/240 volt, single-phase 3-wire multiwire circuits. The neutrals carry only unbalanced current. What adjustment factor applies to the conductors?