Question 13059 of 749 · Maryland Journeyperson Electrician Exam

A 50 A noncontinuous load is supplied by one of six current-carrying THHN copper conductors in a raceway at 30 °C. Terminations are rated 75 °C. What is the smallest conductor size permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 13059

  • C: 6 AWG

Explanation

8 AWG derates to 55 x 0.80 = 44 A, which is below 50 A. 6 AWG derates to 75 x 0.80 = 60 A and its 75 °C rating of 65 A also covers the 50 A load, so 6 AWG is the minimum.

Next to question ›