A motor has a nameplate current of 40 A, a service factor of 1.0 and a temperature rise of 50 °C. What overload rating is required under the basic rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13092
- D: 46 A
Explanation
Motors that have neither a service factor of 1.15 or more nor a temperature rise of 40 °C or less get overloads at 115 % of nameplate current: 40 x 1.15 = 46 A. 50 A is the 125 % value.
More questions: Electrical Calculations
- 13093A motor with a 1.15 service factor and a nameplate current of 24 A trips its overloads during starting. What is the highest overload rating permitted under 430.32(C)?
- 13094A feeder supplies three 460 volt, three-phase motors with table full-load currents of 14 A, 21 A and 34 A. What is the minimum feeder conductor ampacity?
- 13095A 1 hp, 115 volt, single-phase motor has a table full-load current of 16 A. What minimum branch-circuit conductor ampacity is required?
- 13096A feeder supplies three 460 volt motors: 25 hp (34 A) protected by a 90 A inverse time breaker, 15 hp (21 A) and 10 hp (14 A). What is the maximum rating of the feeder overcurrent device?
- 13097What is the Table 430.250 full-load current for a 50 hp, 230 volt, three-phase induction motor?