Question 13096 of 749 · Maryland Journeyperson Electrician Exam
A feeder supplies three 460 volt motors: 25 hp (34 A) protected by a 90 A inverse time breaker, 15 hp (21 A) and 10 hp (14 A). What is the maximum rating of the feeder overcurrent device?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13096
- D: 125 A
Explanation
The feeder device may not exceed the largest branch-circuit short-circuit and ground-fault device plus the sum of the other motors' full-load currents: 90 + 21 + 14 = 125 A. Since 125 A is a standard size it may be used, and rounding up to 150 A is not permitted for feeders.
More questions: Electrical Calculations
- 13097What is the Table 430.250 full-load current for a 50 hp, 230 volt, three-phase induction motor?
- 13098A 7.5 hp, 460 volt, three-phase motor has a table full-load current of 11 A. What minimum branch-circuit conductor ampacity is required?
- 13099Why does the full-load current from Table 430.250, rather than the motor nameplate current, determine motor branch-circuit conductor ampacity for a general-purpose motor?
- 13100A 25 kVA single-phase transformer has a 480 volt primary and a 240 volt secondary. What are the full-load primary and secondary currents?
- 13101What is the full-load secondary current of a 75 kVA, three-phase transformer with a 208Y/120 volt secondary?