Question 13102 of 749 · Maryland Journeyperson Electrician Exam
What is the full-load primary current of a 75 kVA, three-phase transformer with a 480 volt delta primary?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13102
- B: 90.2 A
Explanation
I = 75,000 / (480 x 1.732) = 90.2 A. Treating the transformer as single phase gives 156.3 A.
More questions: Electrical Calculations
- 13103A 45 kVA, three-phase, 480 volt primary transformer (1,000 volts or less) is protected on the primary side only. What is the maximum primary overcurrent device, using the next-higher-standard-size note?
- 13104A single-phase transformer steps 480 volts down to 120 volts. If the primary current is 10 A, what is the secondary current (ignoring losses)?
- 13105A transformer has a turns ratio of 20 to 1 and a primary voltage of 2,400 volts. What is the secondary voltage?
- 13106A balanced three-phase load draws 150 A per phase at 208 volts. What is the minimum transformer kVA required?
- 13107A transformer delivers 48.5 kW to its load while its input is 50 kW. What is its efficiency?
- 13108A 15 kVA, single-phase transformer with a 240 volt primary is protected on the primary side only. Which statement about its primary current is correct?