A 15 kVA, single-phase transformer with a 240 volt primary is protected on the primary side only. Which statement about its primary current is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13108
- D: It is 62.5 A, so the 125 % primary rule applies
Explanation
Primary current is 15,000 / 240 = 62.5 A. Because that is 9 A or more, primary-only protection uses 125 %; the 167 % and 300 % limits apply only to primary currents below 9 A and below 2 A.