A 40 A continuous load is supplied with THWN copper conductors terminating on 75 °C rated equipment. What is the minimum conductor size?

Exactly one answer is correct.

Show solution

Correct answer to question 13110

  • B: 8 AWG

Explanation

The conductor must be rated for 40 x 1.25 = 50 A, and 8 AWG copper is rated 50 A in the 75 °C column. 10 AWG at 35 A fails, and sizing for 40 A without the 125 % factor might tempt someone to use the 90 °C rating of 10 AWG.