Question 13109 of 749 · Maryland Journeyperson Electrician Exam
A branch circuit supplies a 36 A continuous load and nothing else. What is the minimum overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13109
- A: 45 A
Explanation
Overcurrent devices for continuous loads must be rated at least 125 % of the continuous load: 36 x 1.25 = 45 A, which is a standard size. 40 A would only be 111 % of the load.