Correct answer to question 13106
- B: 54.0 kVA
Explanation
kVA = E x I x 1.732 / 1,000 = 208 x 150 x 1.732 / 1,000 = 54.0 kVA. Omitting 1.732 gives the single-phase value of 31.2 kVA.