What is the minimum size aluminum conductor permitted for an underground service lateral serving a general load?

Exactly one answer is correct.

Show solution

Correct answer to question 2026

  • A: 6 AWG

Explanation

Underground service conductors must not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum. A smaller size is allowed only for limited loads such as a single branch circuit. See 230.31(B).