Service conductors installed under a building are considered outside the building when they are covered by at least how much concrete?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2039
- A: 2 in.
Explanation
Conductors installed under not less than 2 in. of concrete beneath a building, or in a raceway encased in at least 2 in. of concrete or brick within the building, are considered outside. Conductors under 18 in. of earth beneath a building also qualify. See 230.6.