Correct answer to question 2041
- A: Outside, or inside nearest the point of entrance of the feeder conductors
Explanation
A building supplied by a feeder needs its own disconnect, readily accessible and located outside or inside nearest the point of entrance of the conductors. See 225.31 and 225.32.