Question 2048 of 749 · Maryland Journeyperson Electrician Exam
Which situation permits an additional service to a building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2048
- C: A separate service for a fire pump
Explanation
Additional services are permitted for special conditions, including fire pumps, emergency and standby systems, parallel power production and similar systems. Load type or a full panelboard is not a reason for a second service. See 230.2(A).
More questions: Services and Service Equipment
- 2049Using the 83 percent rule of the 2020 and 2023 NEC, what minimum copper THWN conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
- 2050A service drop cable with a bare messenger operates at 120/240 volts. What is the minimum clearance above a sidewalk accessible only to pedestrians?
- 2051At a supply voltage of 1000 volts or less, additional services are permitted for capacity reasons when the load exceeds what value?
- 2052A service disconnect supplies only two 2-wire branch circuits. What is its minimum rating?
- 2053What is the minimum depth of working space in front of a 120/240 volt panelboard with live parts on one side and no grounded parts on the other (Condition 1)?
- 2056How is the overcurrent protection for each ungrounded service conductor generally sized?