A service disconnect supplies only two 2-wire branch circuits. What is its minimum rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2052
- D: 30 amperes
Explanation
A two-circuit installation requires a service disconnect rated at least 30 amperes. A single-circuit installation may be 15 amperes. See 230.79(B).
More questions: Services and Service Equipment
- 2053What is the minimum depth of working space in front of a 120/240 volt panelboard with live parts on one side and no grounded parts on the other (Condition 1)?
- 2056How is the overcurrent protection for each ungrounded service conductor generally sized?
- 2057What is the maximum number of disconnects permitted for a building supplied by one outside feeder?
- 2058What is the minimum height above finished grade for the point of attachment of a service drop to a building?
- 2059Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?
- 2061Overhead feeder conductors run from a house to a detached garage at 120/240 volts. What is the minimum clearance above the residential driveway?