What is the maximum number of disconnects permitted for a building supplied by one outside feeder?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2057
- B: Six
Explanation
A building supplied by a feeder may have one disconnect or up to six grouped disconnects. This parallels the service rule. See 225.33.