Question 2053 of 749 · Maryland Journeyperson Electrician Exam
What is the minimum depth of working space in front of a 120/240 volt panelboard with live parts on one side and no grounded parts on the other (Condition 1)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2053
- A: 3 ft
Explanation
For 0 to 150 volts to ground, the working space depth is 3 ft for all three conditions. Higher depths apply only above 150 volts to ground. See Table 110.26(A)(1).