How must a 25 ft feeder tap terminate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3042
- A: In a single circuit breaker or single set of fuses that limits the load to the tap ampacity
Explanation
The 25 ft tap must terminate in a single circuit breaker or single set of fuses that limits the load to the ampacity of the tap. The tap must also be protected from physical damage. See 240.21(B)(2).