A 120/240 volt slash rated circuit breaker may be used on which system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3045
- C: A solidly grounded system where no conductor exceeds 120 volts to ground
Explanation
A slash rated breaker may be used only on a solidly grounded circuit where the voltage of any conductor to ground does not exceed the lower value and the voltage between conductors does not exceed the higher value. See 240.85.