Which of the following is a standard ampere rating for fuses and inverse time circuit breakers?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3050
- A: 110 A
Explanation
Standard ratings include 100, 110 and 125 A. 105, 115 and 120 A are not standard ratings. See 240.6(A).
More questions: Feeders and Overcurrent Protection
- 3051A circuit breaker used to switch 120 volt fluorescent lighting on a regular basis must be marked with which designation?
- 3001Which location is prohibited for an OCPD in all three editions?
- 3002When the handle of a circuit breaker is operated vertically, what position must be the on position?
- 3004A series combination rating may not be used when motors connected between the two devices contribute more than what percentage of the lower-rated breaker's interrupting rating?
- 3005When may a feeder OCPD be sized at 100 percent of the continuous load?
- 3006In which case is the next size up rule not permitted?