A dwelling has an indoor area that is a damp location, such as a covered utility room open to weather. Do 125-volt receptacles there require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4015
- A: Yes, indoor damp and wet locations are listed
Explanation
210.8(A) includes indoor damp and wet locations in the dwelling list. Receptacles in such areas need GFCI protection even though they are inside the building.