Question 4045 of 938 · Maryland Journeyperson Electrician Exam

Under the NEC 2020 and 2023, when an existing dwelling bedroom circuit is extended, a listed outlet branch-circuit AFCI may be used. Where must it be located?

Exactly one answer is correct.

Show solution

Correct answer to question 4045

  • C: At the first receptacle outlet of the existing branch circuit

Explanation

In the 2020 and 2023 editions, 210.12 permitted a listed outlet branch-circuit AFCI located at the first receptacle outlet of the existing branch circuit as one option for extensions. A combination-type AFCI breaker at the origin of the circuit is the other common option.