A 20-ampere branch circuit supplies lighting units and also fastened-in-place utilization equipment. What is the maximum total rating of the fastened-in-place equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4085
- D: 10 amperes
Explanation
210.23 limits the total rating of utilization equipment fastened in place to 50 percent of the branch circuit rating when the circuit also supplies lighting units, cord-and-plug equipment or both. Half of 20 amperes is 10 amperes.