Question 5007 of 749 · Maryland Journeyperson Electrician Exam
A ground ring encircling a building must consist of at least 20 ft of bare copper conductor not smaller than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5007
- C: 2 AWG
Explanation
A ground ring must be in direct contact with the earth, encircle the building, and consist of at least 20 ft of bare copper not smaller than 2 AWG. See 250.52(A)(4).