Question 5021 of 749 · Maryland Journeyperson Electrician Exam

A service has two parallel sets of 3/0 AWG copper (about 168 kcmil each). What is the minimum copper GEC to a water pipe electrode?

Exactly one answer is correct.

Show solution

Correct answer to question 5021

  • A: 2 AWG

Explanation

For parallel sets, the GEC is sized on the equivalent area of the paralleled conductors: 2 x 167.8 kcmil = 335.6 kcmil. That falls in the over 3/0 through 350 kcmil row of Table 250.66, which requires 2 AWG copper.

Next to question ›