Under NEC 2020 and 2023, other than at busbars, a grounding electrode conductor may be spliced only by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5025
- A: Irreversible compression connectors or exothermic welding
Explanation
The GEC must be installed in one continuous length unless spliced with irreversible compression-type connectors listed as grounding and bonding equipment or by exothermic welding. Connections at busbars are also permitted. See 250.64(C).