Question 5032 of 749 · Maryland Journeyperson Electrician Exam

A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?

Exactly one answer is correct.

Show solution

Correct answer to question 5032

  • D: 250 kcmil

Explanation

Above 1100 kcmil copper, the main bonding jumper must have an area of at least 12.5 percent of the largest ungrounded conductor set. 2000 x 0.125 = 250 kcmil. See 250.28(D) and Table 250.102(C)(1).

Next to question ›