Question 5038 of 749 · Maryland Journeyperson Electrician Exam

A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?

Exactly one answer is correct.

Show solution

Correct answer to question 5038

  • B: 10 AWG

Explanation

When ungrounded conductors are increased in size, the EGC must be increased proportionally by circular mil area. 10,380 / 6,530 = 1.59, and 6,530 x 1.59 = 10,380 cmil, which is 10 AWG. See 250.122(B).