Question 5041 of 749 · Maryland Journeyperson Electrician Exam
The EGC for a motor branch circuit is sized from Table 250.122 based on
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5041
- A: The rating of the motor short-circuit and ground-fault protective device
Explanation
For motor circuits, the EGC is based on the rating of the motor branch-circuit short-circuit and ground-fault protective device, not on the overload setting. See 250.122(D).