A ground rod is driven at a parking lot light pole and connected to the pole. How does the Code treat this rod?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5046
- B: Permitted as auxiliary, but the circuit still needs an EGC
Explanation
Auxiliary electrodes are permitted but not required, and the earth may not be used as the effective ground-fault current path. The pole must still be connected to an EGC run with the circuit. See 250.54.