A service has 3/0 AWG copper ungrounded conductors. What is the minimum copper bonding jumper for the interior metal water piping?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5052
- D: 4 AWG
Explanation
The metal water piping bonding jumper is sized from Table 250.102(C)(1) based on the service conductors. For 2/0 or 3/0 copper the jumper must be at least 4 AWG copper. See 250.104(A).
More questions: Grounding and Bonding
- 5053Metal gas piping that is likely to become energized may be bonded by
- 5054For a separately derived system, where is the system bonding jumper installed under the general rule?
- 5055A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?
- 5056The system bonding jumper of a separately derived system is sized based on
- 5057A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
- 5058At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be