Metal gas piping that is likely to become energized may be bonded by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5053
- A: The EGC of the circuit likely to energize it
Explanation
Other metal piping that may become energized must be bonded, and the EGC of the circuit that may energize the piping is permitted to serve as the bonding means. See 250.104(B).