A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5057
- A: A single branch circuit, including a multiwire one, with an EGC
Explanation
A separate building needs its own grounding electrode system unless it is supplied by only one branch circuit, which may be multiwire, that includes an EGC. See 250.32(A).