The system bonding jumper of a separately derived system is sized based on
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5056
- D: The derived ungrounded conductors and Table 250.102(C)(1)
Explanation
The system bonding jumper is sized like a main bonding jumper, using Table 250.102(C)(1) with the size of the derived ungrounded conductors. See 250.30(A)(1) and 250.28(D).