Question 5055 of 749 · Maryland Journeyperson Electrician Exam
A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5055
- C: 2 AWG
Explanation
The GEC for a separately derived system is sized from Table 250.66 based on the derived ungrounded conductors. 250 kcmil copper is over 3/0 through 350 kcmil, so 2 AWG copper is required. See 250.30(A)(5).
More questions: Grounding and Bonding
- 5056The system bonding jumper of a separately derived system is sized based on
- 5057A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
- 5058At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be
- 5059Which of these AC systems is required to be grounded?
- 5060High-impedance grounded neutral systems are permitted for 3-phase AC systems of 480 V to 1000 V where
- 5061Which of the following shall NOT be used to connect EGCs or bonding jumpers to enclosures?