At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5058
- B: Kept isolated from the EGC and enclosure
Explanation
Where an EGC is run with the feeder, the grounded conductor at the separate building may not be connected to the EGC or the grounding electrode system. The EGC is connected to the building electrode system. See 250.32(B)(1).