At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be

Exactly one answer is correct.

Show solution

Correct answer to question 5058

  • B: Kept isolated from the EGC and enclosure

Explanation

Where an EGC is run with the feeder, the grounded conductor at the separate building may not be connected to the EGC or the grounding electrode system. The EGC is connected to the building electrode system. See 250.32(B)(1).