What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 5031

  • C: 2 AWG

Explanation

The main bonding jumper is sized from Table 250.102(C)(1) based on the largest ungrounded service conductor. For copper over 3/0 through 350 kcmil the jumper must be at least 2 AWG copper. See 250.28(D).