Question 5034 of 749 · Maryland Journeyperson Electrician Exam
For a grounded service, the GEC connection to the grounded service conductor is permitted
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5034
- B: Anywhere from the load end of the service drop or lateral up to the service disconnect
Explanation
The connection must be made at an accessible point from the load end of the overhead or underground service conductors up to and including the terminal or bus where the grounded conductor connects at the service disconnecting means. See 250.24(A)(1).