What is the minimum cover for a nonmetallic raceway listed for direct burial without concrete encasement, general condition?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6003
- C: 18 in
Explanation
Nonmetallic raceways such as PVC listed for direct burial without concrete encasement need 18 in of cover under the general condition. See Table 300.5 in NEC 2020 and 2023; the underground installation rules are in 300.7 in NEC 2026.