Rigid metal conduit must generally be secured within what distance of each box or termination?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6021
- A: 3 ft
Explanation
RMC must be secured within 3 ft of each outlet box, junction box, device box, cabinet, conduit body, or other termination. The distance may be increased to 5 ft where structural members do not permit fastening within 3 ft. See 344.30(A).