Trade size 1 rigid PVC conduit must be supported at intervals not exceeding
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6022
- B: 3 ft
Explanation
Table 352.30 requires supports at 3 ft maximum for PVC trade sizes 1/2 through 1, with longer spacing allowed for larger sizes. PVC must also be fastened within 3 ft of each box or termination.