At each outlet or junction box, how much free conductor must be left for splices or device connections?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6049
- A: At least 6 in, extending at least 3 in outside a small opening
Explanation
At least 6 in of free conductor, measured from where it emerges from the raceway or cable, must be left at each box. Where the box opening is less than 8 in in any dimension, the conductor must extend at least 3 in outside the opening. See 300.14.
More questions: Wiring Methods, Conductors and Boxes
- 6050For a straight pull through a pull box containing 4 AWG or larger conductors, the box length must be at least how many times the largest raceway trade size?
- 6051For an angle pull, a trade size 3 and a trade size 2 conduit enter the same wall of a pull box. What is the minimum distance to the opposite wall?
- 6052What is required on every box in a completed installation?
- 6053An enclosure containing a device is supported only by two threaded RMC conduits entering on two sides. Each conduit must be secured within what distance of the enclosure?
- 6054What does the designation THHN indicate?
- 6055What is the temperature rating of THWN-2 insulation in a wet location?