Question 6050 of 749 · Maryland Journeyperson Electrician Exam
For a straight pull through a pull box containing 4 AWG or larger conductors, the box length must be at least how many times the largest raceway trade size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6050
- B: 8 times
Explanation
In straight pulls, the length of the box must be not less than 8 times the trade size of the largest raceway. See 314.28(A)(1).
More questions: Wiring Methods, Conductors and Boxes
- 6051For an angle pull, a trade size 3 and a trade size 2 conduit enter the same wall of a pull box. What is the minimum distance to the opposite wall?
- 6052What is required on every box in a completed installation?
- 6054What does the designation THHN indicate?
- 6055What is the temperature rating of THWN-2 insulation in a wet location?
- 6056XHHW insulation, without the -2 suffix, is rated 90 C in dry and damp locations and what in wet locations?
- 6057Which location is classified as a wet location?