Question 6056 of 749 · Maryland Journeyperson Electrician Exam
XHHW insulation, without the -2 suffix, is rated 90 C in dry and damp locations and what in wet locations?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6056
- D: 75 C
Explanation
XHHW is a cross-linked polymer insulation rated 90 C dry or damp and 75 C wet. XHHW-2 is rated 90 C wet and dry. See the conductor application table in Article 310.
More questions: Wiring Methods, Conductors and Boxes
- 6057Which location is classified as a wet location?
- 6058In NEC 2020 and 2023, aluminum, copper-clad aluminum, or copper conductors may be run in parallel only when they are
- 6063Which use of a flexible cord is prohibited?
- 6066Which location permits Type NM cable?
- 6067In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
- 6068In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than