Question 6068 of 749 · Maryland Journeyperson Electrician Exam
In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6068
- D: Two 6 AWG or three 8 AWG conductors
Explanation
Cables smaller than two 6 AWG or three 8 AWG conductors must be run through bored holes in joists or on running boards. Larger cables may be secured directly to the lower edges of the joists. See 334.15(C).