Where rigid PVC conduit is exposed above grade and subject to physical damage, it must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6071
- C: Identified for the application, such as Schedule 80
Explanation
PVC conduit subject to physical damage must be identified for that use. Schedule 80 PVC is the common identified type. See 352.10(F).