Under NEC 2020 and 2023, what is the minimum size conductor generally permitted for branch circuit wiring in copper?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6060
- D: 14 AWG
Explanation
The general minimum conductor size is 14 AWG copper and 12 AWG aluminum or copper-clad aluminum, with exceptions for items like fixture wire and control circuits. In NEC 2023 this is 310.3(A), and the 2020 edition carries the same rule in Article 310. NEC 2026 lowered the copper minimum, which is why this question is limited to 2020 and 2023.