Question 7006 of 871 · Maryland Journeyperson Electrician Exam

A receptacle is installed under a roofed open porch where it is protected from beating rain (a damp location). What cover is the minimum requirement?

Exactly one answer is correct.

Show solution

Correct answer to question 7006

  • D: A cover that is weatherproof when closed with no plug inserted

Explanation

Section 406.9(A) allows a receptacle in a damp location to have an enclosure that is weatherproof when the receptacle cover is closed and no plug is inserted. The in-use requirement applies to wet locations under 406.9(B). The receptacle itself must still be weather resistant.